June 18, 2017 at 11:21 am #9253
If even half the reports in this Met Article are accurate then no-one should be surprised if subsequent events lead to arrests being made in the very near future.
The role played by the insulation boards in the spread of the fire is self evident and Councils should be developing immediate action plans to strip any building where the insulation board does not meet a Class 0 fire rating. Whether that choice was excusable should be left to the Inquiry but that should not delay immediate remedial action where this is obvious. (using the German or US fire standards might be a good start!)
June 18, 2017 at 1:39 pm #9256“Boris Johnson said in 2009 that safety fears were making the UK safe for ‘extremely stupid people”
“Tory figures congratulated themselves for slashing fire checks for businesses from six hours to just 45 minutes.”
Metro: http://tinyurl.com/ybse44ek
June 18, 2017 at 4:11 pm #9261If even half the reports in this Met Article are accurate then no-one should be surprised if subsequent events lead to arrests being made in the very near future. The role played by the insulation boards in the spread of the fire is self evident and Councils should be developing immediate action plans to strip any building where the insulation board does not meet a Class 0 fire rating. Whether that choice was excusable should be left to the Inquiry but that should not delay immediate remedial action where this is obvious. (using the German or US fire standards might be a good start!)
Too early to jump to conclusions on this until the full facts are known. I may well be someone has been negligent, but suspect a specific set of circumstances laid on top of each other have led to a catastrophic failure. I suspect no one individual will be to blame. It certainly looks like the cladding is the main culprit, but it may well comply with the current building regs. I read somewhere it has a class 0 rating although no doubt lesser than other types of cladding.
There is certainly an issue of erosion of skills and standards in construction generally, pressure on building control depts, clients unwilling to pay for proper supervision (very few people employ clerk of works nowadays).
This is not all linked austerity, it has been ongoing for a number of years before the current government. Hopefully out of this things will change.
There is an obsession with value for money, it is leading to a race to the bottom.
Same name same person
June 18, 2017 at 4:14 pm #9262Its just been on the radio that the cladding was more than likely banned in the UK.
Americans: Over Sexed, Over Payed and Over here, Wat Wat!
June 18, 2017 at 5:25 pm #9270Looking at the damage done it appears that all the windows were upvc which burns very well when hot enough. I suspect the cladding is sufficient to prevent flame coming through the aluminium skin directly to the polystyrene but rising heat would easily get through that.
It really does sound like a total botch job which should never have been given a fire certificate. Not quite sure where the £8M went but don’t think it was spent on cladding.
i7 4790s / 8GB / 480GB SSD / GTX 980 / 34" UltraWide : i3 4170 / 8GB / 480GB SSD / GTX 770 / 24" Samsung : i3 4130 / 8GB / 500GB Spinner / GTX 1050 / 23" Acer : Q9550 / 8GB / 1TB Spinner / GTX 580 / 22" Acer : i7 720QM / 8GB / 1TB+2TB+500GB Spinners (server) : i5 4570 / 8GB / 60GB SSD / 1TB / GeForce 210 / 22" Dell It's getting warm in here!
June 18, 2017 at 5:35 pm #9272Would be nice to deal with peoples needs right now and also start a much needed enquiry before marching for the government to fall dont you think ?
June 18, 2017 at 5:40 pm #9273Its just been on the radio that the cladding was more than likely banned in the UK.
Philip Hammond (no less) made that ‘helpful’ remark.
A synopsis of the Building Regs is on this link.
” Approved Document B of the Building Regulations for England and Wales, Section 2 of the Technical Handbook Scotland, and Technical Booklet Part E for Ireland all make reference to the requirements for the safe design of high-rise buildings. Approved Document B4, Section 12 states: “The external envelope of the building should not provide a medium for fire spread if it is likely to be a risk to health or safety. The use of combustible materials in the cladding system and extensive cavities may present such a risk in tall buildings.”
It seems perfectly clear to me, the insulation panels must be in full compliance with BR135 B, and the materials used should also be in full compliance.
The Beeb quoted that the insulation of this board comprises of polyethylene fibres. Assuming this report was accurate then I would have thought the material completely fails on two counts . First it is most definitely flammable, and second the use of flammable fibres will almost certainly give rise to a disasterous wicking effect that will accelerate the vertical propagation of the fire.
June 18, 2017 at 6:46 pm #9277I was waiting for this thread to come along. I’m really intrest in what drezha makes of this.
June 18, 2017 at 6:56 pm #9279I am waiting for the results of a propper enquiry. Knee reaction is for ten year olds and the usuall marks bross
June 18, 2017 at 6:58 pm #9280I am waiting for the results of a propper enquiry. Knee jerk reaction is for ten year olds and the usuall marks bross tits.
June 18, 2017 at 7:29 pm #9287Philip Hammond is currently attacking his own party of government on all fronts: https://tinyurl.com/yao8f6r5
Quite obviously wants the Tob Job when (if?) May bites the dust. He should check her record. She has outfought and outlasted some heavyweights on her way up.
As Graham says, no point in speculating about blame and root causes until an Inquiry has jumped through all the hoops. It is a terrible, monstrous incident, the deaths and injuries are horrendous. However, if you listen and observe closely over the coming months, you may hear and observe the signs of CYA on a grand scale.
The understandable anger of the people involved, their relatives, friends and neighbours, is going to keep this one alive for some time.
When the Thought Police arrive at your door, think -
I'm out.June 18, 2017 at 7:44 pm #9290Hammond clearly sets out that the cladding is banned everywhere and he believes it to be banned in the UK. He sets out two requirements for the inquiry pretty clearly.
In my view regardless whether he wants the job (fool if he wants that poisoned chalice), it is obvious that the public is in no mood for political obfuscation. Good for him that he saw the need for plain speech even if it results in jail for a lot of Tory chums in Chelsea.
June 18, 2017 at 8:09 pm #9293Thanks for that Ed, I apologise to Mr H. He does seem to be deciding to make statements that no other Minister or government figure will make. He has my respect for telling the truth.
Now check out the latest evidence of BoJo stupidity:
Scroll down to the first “2013” comment. How his words have come back to haunt him, why cannot the PM see that the man is a walking time-bomb?
When the Thought Police arrive at your door, think -
I'm out.June 18, 2017 at 10:20 pm #9299A subject that I’ve been avoiding on here because frankly, I’ve been dealing with it elsewhere. At least no one here has jumped on the lefty “social cleansing” conspiracy theory that I’ve seen on Facebook. And no one has mentioned sprinklers or given me grief about single stair flats or point blank accused me of being a killer.
Firstly, Class 0 materials don’t actually exist – though technically, the requirements are met by being incombustible. Materials such as mineral fibre achieve this, but need some form of support which may be combustible. This should be tested to BS 8414. Buildings over 18m with a boundary greater than 1m distant can be Class 0, or Class 1 (with additional specifications). So in theory, you can have a combustible material on the side of the building fine. The Class rating comes from a BS 476 flame spread test, which measures the flame spread across a material. I used to work (before moving to Manchester) for the firm that does various testing (and wrote BR 135).
In terms of who is at fault, I think that no one will end up going to court because it’ll come down to a number of people having a minor role in causing the issues. The building may have been treated as a material alteration, rather than a material change of use when it had planning granted for the refurb works. This will mean that the current Building Regs would not be required to be met, only that the works made the building “no worse” than existing. That would be a Building Control (having worked with RBKC Building Control, they’re quite fastidious so it may have been an Approved Inspector). That might have had an effect. The contractor may have installed the panels badly, negating the fire protection (as there should be fire protection to prevent fire entering the walls and cavities). The biggest issues will come if the contractors deliberately misled on what cladding was fitted. The management company will come under flak for their fire risk assessments and if that was carried out by a competent person on behalf of the management company, then they would likely find themselves under fire (and possible imprisoned – as a fire risk assessor, I can be fined and sent to prison for poor fire risk assessments so from dropping a 6 hour inspection down to 45 minutes as one of the earlier links is just crap. Maybe if they’re a cowboy.) Mind, fire risk assessments of flats only cover what is within the common spaces, so if there’s issues between two flats, it’ll never be picked up. The fires appeared to be inside and outside the building from what I’ve seen – how the fire spread back in needs to be investigated. Or if it spread internally, it needs to be investigated. I’ve heard rumours (and until it’s proven, it’s a rumor), that gas works had been undertaken. Chances are, they breached compartment walls. Which are usually designed to prevent spread of smoke and fire into surrounding areas – currently flats are designed to contain it for 60 minutes.
As mentioned elsewhere, there is also a skills shortage in the construction industry and fire resisting materials are required to be installed exactly as per the instructions otherwise they wont work. I’ve even seen competent installers cock things up and I had to pick this up in a fire risk assessment.
No chance of using the US codes. They’re a mess and likely wouldn’t have helped – Dubai was built to the same standards and they’ve had issues with cladding.
No doubt we will see some updates to the guidance for fire (so an update to the Approved Document) but I doubt the Building Regulations will be updated (because they’re about 8 pages and the bit relating to fire essentially says “Buildings should be safe in a fire”. However, we’ve had new guidance issued (and updated) since ADB was updated – BS 9991 (Flats) and BS 9999 (Buildings other than Flats). So not sure what will be updated.
My old colleagues will no doubt be appointed to carry out the investigations and I wish them all the best (I’d probably be involved as well, had I not left last month!)
"Everything looks interesting until you do it. Then you find it’s just another job" - Terry Pratchett
June 18, 2017 at 10:35 pm #9303Drezha,
My congratulations for the most comprehensive summary of the whole affair.
I too have read FB with many already shouting to have the Block torn down – with the human remains still inside?
There are far too many people coming in with their own ‘barrack room lawyer’ ideas but few if any have any intelligent things to say.
It will be a matter of time, detained inquiries, many questions asked – I hope the public enquiry recently announced will also have the power to compel those involved to attend and, unless self-incriminating, to give evidence.
The more you meet people the more you understand why Noah took animals instead of humans
June 18, 2017 at 10:44 pm #9304As mentioned elsewhere, there is also a skills shortage in the construction industry and fire resisting materials are required to be installed exactly as per the instructions otherwise they wont work. I’ve even seen competent installers cock things up and I had to pick this up in a fire risk assessment.
This is an issue at the moment on some sites I have worked on, there is not the skills to sign off work properly and firms abdicate responsibility to the specialist installer. Its penetrations through the compartmentation that cause me most concern on projects, particularly where things get hidden. Fire stopping in the external wall cavity is another one, there are always a few difficult areas to detail. How can you tell whether every joint is built correctly when hidden by the panels.
The trouble is the market perpetuallly wants to squeeze money out of projects, including consultants and dont want to pay for a full service. The biggest loss to the industry is a clerk of works.
This along with the problem with schools in Scotland (collapsed walls), is indicative of stored up problem where the chickens will come home to roost eventually.
We have lost too many skilled people through successive recessions and obsession with cost inefficiencies.
Same name same person
June 19, 2017 at 8:23 am #9308The inquiry will eventually confirm their views of probable causes of the inferno but it appears that an event inside one apartment on the seventh floor was sufficiently severe to ignite the external cladding.
According to this report (and confirmed by other different sources) the fire initiated when a refrigerator exploded following an electrical fault. I assume this means that the fridge was leaking propane a moderately common event due to improper fitting/damage/faults. The building itself was also reportedly suffering frequent major power surges that actually destroyed electrical equipment in apartments so a power surge may possibly have initiated an electrical fire that in turn ignited an explosive propane-air mixture within the kitchen unit.
TBH I think that although a kitchen fire is a frightening event, it is a fairly common occurrence as a result of various very different events. Of most importance is how an internal kitchen fire ignited the cladding situated outside the kitchen window and the consequent implications for building materials and the provision of domestic fire-fighting equipment (fire blankets, small extinguishers etc) within apartments
The cladding should have been in accordance with the Building Regs set out in simple terms below:
“The guidance note includes three options for compliance with BR 135 and Approved Document B:
Option 1 The use of materials of limited combustibility for all elements of the cladding system both above and below 18m. This includes the insulation, internal lining board and the external facing material. Smaller gasket parts and similar low-risk items can be excluded from this requirement.(A polyethylene core obviously fails this provision, so options 2 and 3 are the only way it could have been approved)
Option 2 The client submits evidence to Building Control that the complete proposed external cladding system has been assessed according to the acceptance criteria in BR 135 – that is, the fire tests in BS 8414 Part 1 or 2. The test should be carried out by an independent UKAS-accredited testing body. (If it did pass such a test then the test procedure is obviously faulty and needs to be changed.
Option 3 If no actual fire test data exists, a desktop study report from a qualified fire specialist should be undertaken.” (This is the big weak point of the Building Regs., pass or fail depends on the knowledge and experience of the specialist, however any such opinion such have comprehended experience of this material elsewhere in the UK/World where it was known to have failed).
Some of these outcomes obviously lead to criminal prosecutions. To some extent this is irrelevant to the current situation. Regardless of all else, it is self-evident that this material is unsafe as all the cladding in every location on the building above ~70 feet was damaged by fire. It would be sensible to immediately address this problem and identify all other buildings at risk.
June 19, 2017 at 10:40 am #9310I was trying to explain to the Mrs last night that the fire shouldn’t have come into the building from outside. I’m not totally sure of this because all the windows appear to be missing on the building, even ones on the edge of where the fire was so I suspect they were flammable or easily melted. Many of the flats seem to have large windows with multiple rooms so it may be that the fire spread through one window and out another or perhaps people left their front doors open because the fire was outside and the building updraught drew the fire in that way. It is counter-intuitive that with a fire outside you’d be safer if you shut your front door – the only escape route.
i7 4790s / 8GB / 480GB SSD / GTX 980 / 34" UltraWide : i3 4170 / 8GB / 480GB SSD / GTX 770 / 24" Samsung : i3 4130 / 8GB / 500GB Spinner / GTX 1050 / 23" Acer : Q9550 / 8GB / 1TB Spinner / GTX 580 / 22" Acer : i7 720QM / 8GB / 1TB+2TB+500GB Spinners (server) : i5 4570 / 8GB / 60GB SSD / 1TB / GeForce 210 / 22" Dell It's getting warm in here!
June 19, 2017 at 12:37 pm #9313I agree that a lot of additional factors/causes should be considered at the Public Inquiry, but I think the scale of this disaster is similar to that of an air accident. In that situation if those involved identify a potentially common issue there is an immediate inspection recall on all similar aircraft and immediate remedial action taken. The air accident inquiry proceeds at its own pace and could take months/years to complete. I’m thinking for example of the Air France tragedy off Brazil, the recall for inspection/modification of air-speed pitot tubes was done within weeks of the accident, the air accident inquiry took many months more as the aircraft frame etc had to be found.
Maybe this is a case where the HSE could earn its salt for once and issue appropriate prohibition orders. Someone needs to step up to the plate – the ‘strong & stable’ Government has already shown itself to be totally incapable of such action.
June 19, 2017 at 3:46 pm #9316Maybe this is a case where the HSE could earn its salt for once and issue appropriate prohibition orders. Someone needs to step up to the plate – the ‘strong & stable’ Government has already shown itself to be totally incapable of such action.
HSE wouldn’t have anything to do with it, because it’s not a workplace and doesn’t fall under the HSE regulations, except perhaps where the building is staffed.
The legislation exists to do so mind – it falls to the Fire and Rescue Services though. Issues could be raised under the Regulatory Reform (Fire Safety) Order 2005 and the brigades could raise enforcement notices against the buildings (which requires work to be updated within a specific time frame) or even a prohibition notice that would either limit or prevent people accessing part or all of a building.
"Everything looks interesting until you do it. Then you find it’s just another job" - Terry Pratchett
-